About three-phase to ground fault and line disconnection #249

Answered by cuihantao
Crishawy asked this question in Q&A
Discussion options

You must be logged in to vote

After some initial investigation, I found two related issues:

  1. As mentioned, all bus voltages are restored when the fault gets cleared. Bus 6 and 8 voltages are restored as well.
  2. The power flow solutions can be attracted to the low-voltage or the high-voltage one, depending on the initial voltage values.

When voltages are restored at 0.13 s, the system without bus 7 finds a high-voltage power flow. That's the reason the left figure has voltage changes on buses 6 and 8.

When voltages are not restored, the system does not have a good initial value to restore to the high-voltage solution after 0.2 s. All voltages remain low, as shown in your right figure.

The workaround is to clear the faul…