Question about Initialization #419

Answered by cuihantao
xiaoheimai95 asked this question in Q&A
Discussion options

You must be logged in to vote

Thank you for posting the discussion.

There was just one missing data when you set up the wind models. When replacing synchronous generators with REGCA1, make sure that latter has the same capacity rating Sn. The Sn=100 in your case causes some per-unit values of the controllers to be well beyond typical limits. That was the case for the current limiter REECA1.HpHL_lim.

Here's the case with the fix. I came up with the Sn for REGCA1 by following that of synchronous generators.

ieee39_add_wind.xlsx

Replies: 1 comment 1 reply

Comment options

You must be logged in to vote
1 reply
@xiaoheimai95
Comment options

Answer selected by xiaoheimai95