Question about Initialization #419
Answered
by
cuihantao
xiaoheimai95
asked this question in
Q&A
-
Beta Was this translation helpful? Give feedback.
Answered by
cuihantao
Mar 10, 2023
Replies: 1 comment 1 reply
-
Thank you for posting the discussion. There was just one missing data when you set up the wind models. When replacing synchronous generators with REGCA1, make sure that latter has the same capacity rating Here's the case with the fix. I came up with the |
Beta Was this translation helpful? Give feedback.
1 reply
Answer selected by
xiaoheimai95
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Thank you for posting the discussion.
There was just one missing data when you set up the wind models. When replacing synchronous generators with REGCA1, make sure that latter has the same capacity rating
Sn
. TheSn=100
in your case causes some per-unit values of the controllers to be well beyond typical limits. That was the case for the current limiterREECA1.HpHL_lim
.Here's the case with the fix. I came up with the
Sn
for REGCA1 by following that of synchronous generators.ieee39_add_wind.xlsx