Generation trip: Generator desconection vs PV gen desconection, RenGen trip doesn't work #558
-
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 2 replies
-
Hi Amparo, Which renewable generator are you using? Probably it's not coded yet to take status changes. Also, tripping a conventional generator and a renewable generators will have the same result, if they are initialized at the same initial power flow. |
Beta Was this translation helpful? Give feedback.
-
Consider two scenarios where you connect a conventional generator and REGC_1, respectively. If the two generators are initialized from the same static PV, disconnecting the generator in either case will result in the same instantaneous reduction of power, so the response is expected to be the same.
You can try editing the power output equation in the renewable generator by multiplying |
Beta Was this translation helpful? Give feedback.
Consider two scenarios where you connect a conventional generator and REGC_1, respectively. If the two generators are initialized from the same static PV, disconnecting the generator in either case will result in the same instantaneous reduction of power, so the response is expected to be the same.
You can try editing the power output equation in the renewable generator by multiplying
u
. Whenu
goes to zero, the…