I have a question regarding the delta in heating. I have a Series K pump. The temperature is set to 22°C, and the delta is 2°C. The heating turns off at 24°C and turns on at 19°C. How is this calculated? Because I get +2°C and -3°C. |
Beta Was this translation helpful? Give feedback.
Replies: 4 comments 22 replies
-
How your pomp is set ? Is it temperature of water outlet , or yuo are using internal thermostat ? |
Beta Was this translation helpful? Give feedback.
-
So what is your temperature in rooms then , if your outlet temp is max 24 deg ( 3min and off ,so more of the time 23 or less). As i recall this function correctly..... So when your target temp is 22 , HP starts modulating to keep it. When modulation is not enough , and temperature reach more then 2deg of target ( basicly 2.25deg is enough) then after 3min HP will switch off ( or temp will drop to 2 deg difference or less). But during stop HP remembers the Inlet temperature. And this Inlet temperature is now reference , and have to drop again 2 deg before this reference to turn compressor on. So it could be like this , that your outlet is like 24,25deg , but your inlet has only 21deg , and HP wait to have it 19deg to turn on again... |
Beta Was this translation helpful? Give feedback.
-
Delta is only to maintain inlet/outlet proportion.. it will drive circulation pump to maintain that different. And off indicator is inlet temperature.. if it reaches outlet temperature then it indicate pump to switch off. Whole logic is very well described in service manual. |
Beta Was this translation helpful? Give feedback.
-
I decided to analyze the condition for restarting the pump: Water Outlet Temperature – Water Inlet Temperature Substituting, we get: After rearranging the formula, we get: So it seems I wasn’t mistaken after all—delta also has an impact on turning the pump back on. |
Beta Was this translation helpful? Give feedback.
Here is snipet from service manual:
continuously 3 minutes.
(temperature at thermostat OFF is triggered) <-3°C