Delta in heat pump heating #562

Answered by geduxas
krzbor asked this question in Q&A
Oct 22, 2024 · 4 comments · 22 replies
Discussion options

You must be logged in to vote

Here is snipet from service manual:

  • Compressor is OFF when Water Outlet Temperature – Internal Water Setting Temperature > 2°C for
    continuously 3 minutes.
  • Compressor is ON after waiting for 3 minutes, if the Water Outlet Temperature – Water Inlet Temperature
    (temperature at thermostat OFF is triggered) <-3°C