You signed in with another tab or window. Reload to refresh your session.You signed out in another tab or window. Reload to refresh your session.You switched accounts on another tab or window. Reload to refresh your session.Dismiss alert
Hi, the following observation is not about an error in OpenDTU, but rather of a suspicious malfunction the HM-1500 inverter itself. Nevertheless I would like to share my observation with this OpenDTU/Hoymiles community, as OpenDTU helped me to trace it down:
My system consists of a Hoymiles HM-1500 and 4 identical PV panels, each with 395 Wp. PV panel "A" faces southward at 45 degree, while PV panels "B", "C", "D" face eastward at 60 degree. The panels A-D are connected to the inputs 1-4 of the HM-1500 as A-1, B-2, C-3, D-4. This system is monitored with OpenDTU and has been running stable and nicely for about 15 months.
After a summer holiday I noticed that the daily AC peak power had been reduced during the previous days, to about 3/4 compared to its usual size. "String 1" reported only about 0,9 W during direct sunshine and the Event Log showed the message "PV-1: No input".
I interchanged the wiring of A and B from A-1,B-2 to A-2,B-1 and found then about 0,8 W on String 2, and "PV-1: No input". I interchanged the wiring of A and C from A-1,C-3 to A-3,C-1 and observed about 0,7 W on String 3 and Event Log "PV-2: No input". Going back to wiring A-1,B-2,C-3,D-4 yielded the original observation: low/no DC power on String 1 and "PV-1: No input". Grid disconnection and/or inverter restart via OpenDTU did not change the behaviour of the HM-1500.
I concluded that PV panel A would be defective and the HM-1500 was OK.
Then I measured the open circuit voltage "Voc" and the short circuit current "Isc" of all four panels using a multimeter.
Results: Voc around 40-45 Volt for all four panels, Isc at 9.59, 2.5, 2.5, 2.5 Ampere for panels A, B, C, D.
Conclusion: all four panels behaved faultlessly, with Isc values in approximate accordance with the angle of the sun at afternoon time.
During this Isc measurement, the HM-1500 was disconnected from the AC grid and also disconnected from all 4 DC inputs simultaneously. Previously, the HM-1500 had always been connected to at least one of the DC-inputs.
After reconnecting all panels as A-1, B-2, C-3, D-4 and reconnecting the HM-1500 to the grid, I made the following stunning observation. At first: Event Log "PV-1: No input" and no/low DC power on String 1, normal power on String 2-4, i.e. same problem as before. But then after very few minutes (approx. < 5-6 minutes): Suddenly all four DC Strings are back at reporting normal/expected DC power(!).
My conclusion: the HM-1500 was temporarily in a complete dead-voltage state, and this helped it recover its normal function?!
My question: Is it maybe problematic for the HM-1500 that panels A and B at input strings 1 and 2 can have greatly varying DC power (370 W vs. 70 W, or vice versa) during the course of the day because of the 90 degree difference in horizontal inclination towards the sun (east vs. south)?
reacted with thumbs up emoji reacted with thumbs down emoji reacted with laugh emoji reacted with hooray emoji reacted with confused emoji reacted with heart emoji reacted with rocket emoji reacted with eyes emoji
-
Hi, the following observation is not about an error in OpenDTU, but rather of a suspicious malfunction the HM-1500 inverter itself. Nevertheless I would like to share my observation with this OpenDTU/Hoymiles community, as OpenDTU helped me to trace it down:
My system consists of a Hoymiles HM-1500 and 4 identical PV panels, each with 395 Wp. PV panel "A" faces southward at 45 degree, while PV panels "B", "C", "D" face eastward at 60 degree. The panels A-D are connected to the inputs 1-4 of the HM-1500 as A-1, B-2, C-3, D-4. This system is monitored with OpenDTU and has been running stable and nicely for about 15 months.
After a summer holiday I noticed that the daily AC peak power had been reduced during the previous days, to about 3/4 compared to its usual size. "String 1" reported only about 0,9 W during direct sunshine and the Event Log showed the message "PV-1: No input".
I interchanged the wiring of A and B from A-1,B-2 to A-2,B-1 and found then about 0,8 W on String 2, and "PV-1: No input". I interchanged the wiring of A and C from A-1,C-3 to A-3,C-1 and observed about 0,7 W on String 3 and Event Log "PV-2: No input". Going back to wiring A-1,B-2,C-3,D-4 yielded the original observation: low/no DC power on String 1 and "PV-1: No input". Grid disconnection and/or inverter restart via OpenDTU did not change the behaviour of the HM-1500.
I concluded that PV panel A would be defective and the HM-1500 was OK.
Then I measured the open circuit voltage "Voc" and the short circuit current "Isc" of all four panels using a multimeter.
Results: Voc around 40-45 Volt for all four panels, Isc at 9.59, 2.5, 2.5, 2.5 Ampere for panels A, B, C, D.
Conclusion: all four panels behaved faultlessly, with Isc values in approximate accordance with the angle of the sun at afternoon time.
During this Isc measurement, the HM-1500 was disconnected from the AC grid and also disconnected from all 4 DC inputs simultaneously. Previously, the HM-1500 had always been connected to at least one of the DC-inputs.
After reconnecting all panels as A-1, B-2, C-3, D-4 and reconnecting the HM-1500 to the grid, I made the following stunning observation. At first: Event Log "PV-1: No input" and no/low DC power on String 1, normal power on String 2-4, i.e. same problem as before. But then after very few minutes (approx. < 5-6 minutes): Suddenly all four DC Strings are back at reporting normal/expected DC power(!).
My conclusion: the HM-1500 was temporarily in a complete dead-voltage state, and this helped it recover its normal function?!
My question: Is it maybe problematic for the HM-1500 that panels A and B at input strings 1 and 2 can have greatly varying DC power (370 W vs. 70 W, or vice versa) during the course of the day because of the 90 degree difference in horizontal inclination towards the sun (east vs. south)?
Any thoughts about this, or similar obvervations?